Amendments to the Industrial Safety and Health Law etc
Overview of Partial Amendments to the Industrial
Safety and Health Law, Ordinance on
Industrial
Safety and Health, Ordinance on the
Safety
of Boilers and Pressure Vessels, Ordinance
on the Safety of Cranes, Etc., and
Ordinance
on the Safety of Gondolas
Partial amendments to the Industrial
Safety
and Health Law and other related ordinances
were recently enacted. The major modifications
compiled by JICOSH are as follows:
|
I. Industrial Safety and Health Law
1. Notification of information on the toxicity, etc., of chemical substances,
etc.
|
(1) |
As a number of industrial accidents due to
chemical substances are still occurring,
it is important to prevent these accidents
by communicating useful information on the
toxicity, etc., of chemical substances to
workplaces, in order to allow these workplaces
to take appropriate measures for the prevention
of health impairment.
Accordingly, to facilitate the adoption of
effective measures to prevent health impairment
due to chemical substances to workers, the
law was amended to stipulated that when chemical
substances, etc., are to be transferred or
provided, those who transfer or provide such
substances must provide information on the
toxicity, etc., of such substances to the
recipients of such substances.
|
(2) |
Notification of the information above must
be made for each chemical substance
to be
transferred or provided.
|
2. Announcement of guidelines on the necessary measures to prevent health
impairment to workers due to chemical substances, etc.
|
|
The Minister of Labour is to announce guidelines
on the measures that must be taken by employers
to prevent health impairment to workers due
to chemical substances, etc. and is to provide
the necessary guidance and assistance for
this purpose.
|
3. Purpose of MEDICAL EXAMINATIONS BY WORKERS OWN INITIATIVES for workers
engaged in night work
|
|
The purpose of the voluntary medical examination
(hereinafter called "MEDICAL EXAMINATIONS
BY WORKERS OWN INITIATIVES") system for
workers engaged in night work (hereinafter
called "NIGHT WORKER") is as follows: When
NIGHT WORKERS who are concerned with their
health may voluntarily undergo medical examinations
without waiting for the next medical examination
for workers engaged in specified work (hereinafter
called "SPECIFIED WORK MEDICAL EXAMINATIONS"),
and their employers are required to take
post-examination measures for such workers
in the same way as for the results of SPECIFIED
WORK MEDICAL EXAMINATIONS when the workers
submit the results of such MEDICAL EXAMINATIONS
BY WORKERS OWN INITIATIVES.
|
4. Providing workers with information on the toxicity, etc., of chemical
substances
|
|
In order to prevent industrial accidents
involving chemical substances because workers
handling such substances are not provided
with information concerning the contents,
toxicity and precautions required in handling
same, information on such toxicity and other
necessary matters shall be provided to workers.
|
II. Ordinance on Industrial Safety and Health
1. Improvement of health control for NIGHT
WORKERS
|
(1) |
The results of MEDICAL EXAMINATIONS BY WORKERS
OWN INITIATIVES and matters relating to the
establishment of measures to deal with such
results are added to the terms of reference
for health committees.
|
(2) |
Workers who are entitled to submit a certificate
showing the results of MEDICAL EXAMINATIONS
BY WORKERS OWN INITIATIVES shall be those
workers who are regularly employed and who
have been engaged in NIGHT WORK four or more
times per month on average during six months
prior to such MEDICAL EXAMINATION BY WORKERS
OWN INITIATIVES.
|
(3) |
The workers described in Item (2) above may submit to their employers a
physician's certificate showing the results of the medical examination
performed by said physician in relation to all or part of the survey items
contained in past medical and work history records, provided that the certificate
is submitted within three months after the date of such examination.
|
(4) |
The certificate showing the results of the
MEDICAL EXAMINATION BY WORKERS OWN INITIATIVES
must indicate the results for each item of
said medical examination performed on the
relevant worker.
|
(5) |
Employers are required to prepare an individual
medical examination sheet for each
worker
on the basis of the results of said
medical
examinations, and safe keep such sheets
for
five years.
|
(6) |
A hearing at which information can be presented
by a physician who has prepared a certificate
showing the results of a medical examination
must be conducted within two months from
the date on which the relevant worker submits
such a certificate to the employer. |
III. Ordinance on the Safety of Boilers and
Pressure Vessels
1. Purpose of Amendment
|
|
If boilers, class I pressure vessels, mobile
cranes and gondolas are not installed after
undergoing structural inspections, manufacturing
inspections or usage inspections (hereinafter
called "MANUFACTURING INSPECTIONS") and
the director of the relevant prefectural
labour office certifies that such equipment
has been stored in good condition during
the period it is not installed, the period
after which such equipment may be installed
without undergoing usage inspections may
be extended. The effective term of inspection
certificates for mobile boilers, mobile cranes
and gondolas may likewise be extended.
|
2. Points of Amendment
|
(1) |
Usage inspection
For boilers, class I pressure vessels, mobile
cranes and gondolas for which the director
of the prefectural labour office certifies
that they have been stored in good condition
after the MANUFACTURING INSPECTIONS (hereinafter
called "APPROVAL"), the period after which
such equipment may be installed without undergoing
usage inspections is extended to two or more
years from one or more years for boilers,
class I pressure-vessels and gondolas, and
three or more years from two or more years
for mobile cranes.
|
(2) |
Effective term of inspection certificate
For mobile boilers and gondolas to which
APPROVAL is granted, the effective term of
the inspection certificate may be extended
up to one year from the installation date
but not exceeding two years after the MANUFACTURING
INSPECTION, and for gondolas to which APPROVAL
were granted, the effective term may be extended
up to two years from the installation date
but not exceeding three years after the MANUFACTURING
INSPECTION.
|
(3) |
Other
The director of the prefectural labour office
shall grant approval certificate to manufacturers
or importers of specified machines, etc.,
who are believed to have maintained such
machines in good condition or to individual
specified machines, etc., that are believed
to have been stored in good condition.
|
The procedures relating to such APPROVAL
and the treatment of approved specified machines,
etc., are set forth in Attachment 1. |
Attachment 1
Procedure Relating to APPROVAL and Treatment
of Approved Specified Machines, Etc.
1. APPROVAL Relating to Storage
|
|
Directors of prefectural labour offices are
authorized to issue APPROVAL certificates
in accordance with the following procedures
for manufacturers or importers of specified
machines, etc., who are recognized as having
the capability of carrying out storage of
same in good condition, or individual specified
machines, etc., that are recognized as being
stored in good condition.
|
(1) APPROVAL of workplaces
|
A. |
APPROVAL application
When applying for APPROVAL, manufacturers or importers (hereinafter called
"APPLICANT") of specified machines, etc., shall submit an approval
application form (Form No.1 = omitted) relating to the storage of said
specified machines, etc. for each workplace, along with the rules (hereinafter
called "STORAGE RULES") for their storage after undergoing MANUFACTURING
INSPECTIONS to the director of the prefectural labour office having jurisdiction
over the APPLICANT's address (hereinafter called "DIRECTOR HAVING
JURISDICTION").
|
B. |
APPROVAL inspection
The relevant DIRECTOR HAVING JURISDICTION
shall carry out site surveys, if necessary,
and determine whether or not an APPROVAL
should be granted to the APPLICANT on the
basis of the results of pertinent documents
and site inspections.
The relevant DIRECTOR HAVING JURISDICTION
shall notify the APPLICANT of the APPROVAL
decision by providing the APPLICANT with
an approval certificate relating to the storage
of the specified machines, etc., (Form No.2
=omitted) or a certificate of the results
of approval inspections relating to the storage
of such machines, etc., (Form No.3 = omitted).
|
C. |
APPROVAL standards
The standards on which an APPROVAL decision
is made shall be established in the Appendix.
|
D. |
Effective term of APPROVAL
An APPROVAL shall be effective for five years
from the date on which the APPROVAL is granted.
|
E. |
APPROVAL renewal
An approval renewal application form (Form
No.5 = omitted) shall be submitted to the
relevant DIRECTOR HAVING JURISDICTION when
requesting the renewal of the effective term
for the storage of specified machines, etc.,
along with the related STORAGE RULES. (An
approval renewal application form may be
submitted without attaching STORAGE RULES
if there are no changes in the contents of
such Rule by indicating such fact on the
application form.)
The provisions relating to the APPROVAL inspection
(Item B above) shall also be applied to approval
renewal applications.
A renewed APPROVAL shall be effective for
five years from the date on which the original
effective term expires. However, the effective
term for renewal shall be five years from
the date on which the original APPROVAL is
granted if the renewal application is submitted
more than one year before the expiration
date of the previous approval.
|
F. |
Change in contents of APPROVAL
When an applicant to whom an APPROVAL is
granted wishes to change the contents of
its STORAGE RULES, the applicants shall submit
an approval modification application form
(Form No.4 =omitted) to the relevant DIRECTOR
HAVING JURISDICTION, along with a copy of
the modified STORAGE RULES.
The provisions relating to the APPROVAL inspection
(Item B above) shall also be applied to approval
modification applications.
The effective term for an already granted
APPROVAL cannot be changed even if such APPROVAL
is changed.
|
G. |
Revocation of APPROVAL
The relevant DIRECTOR HAVING JURISDICTION
may revoke an APPROVAL granted to a workplace
if such workplace falls under any of the
following:
(a) |
It no longer meets the standards specified
in the Appendix. |
(b) |
It has changed its STORAGE RULES without
acquiring approval for change prescribed
as in Item E. |
(c) |
It has stored machines in a way that differs
from the STORAGE RULES it has submitted.
|
The revocation of APPROVAL pursuant to this
notification shall be made in accordance
with the procedures specified in the Administrative
Procedure Law (Law No. 88 of 1993), as such
revocation falls under the disadvantageous
treatment as stipulated in the Law. In addition,
such revocations must be reported to the
Ministry of Labour.
|
(2) APPROVAL of individual machines, etc.
|
A. |
APPROVAL application
In the event that those (hereinafter called
"CUSTODIAN") who are storing specified
machines, etc., that have undergone MANUFACTURING
INSPECTIONS intend to request an APPROVAL
for the storage of individual specified machines,
they shall submit an approval application
form (Form No.6 = omitted) concerning the
individual machines and covering the storage
conditions for such specified machines, etc.,
to the director of the prefectural labour
office having jurisdiction over the workplace
in which such specified machines are stored,
along with documents indicating the pertinent
storage conditions after such machines have
undergone MANUFACTURING INSPECTIONS.
|
B. |
APPROVAL inspections
Inspections for APPROVAL shall be made in
the same way as for Items (1)-B and C above.
|
2. Treatment of Specified Machines. Etc.,
Approved
|
(1) Treatment of boilers (excluding mobile
boilers; hereinafter the same in this clause)
and class I pressure vessels
|
A. |
An installation notification of boilers or
class I pressure vessels may be accepted
if such notification is accompanied by the
following documents and two years have not
elapsed since completing the MANUFACTURING
INSPECTIONS for the relevant specified machines,
etc. In such cases the submission date of
such installation notifications must be within
one month after the confirmed date on which
such storage was completed.
(a) |
Manufacturers or importers acquiring APPROVALS
for workplace:
A copy of the approval notification
relating
to the storage of the
specified machines, etc., (Form
No.2)
A document demonstrating that
the specified
machines, etc., have been stored
in good
condition
|
(b) |
CUSTODIANS acquiring the APPROVALS for individual
machines, etc.:
An approval notification relating
to the
storage conditions of the
specified machines, etc., (Form
No.7)
|
|
B. |
In the event that the installation notification
is accepted, the ledger shall record
in the
Remarks column that said equipment
is an
approved specified machine.
|
(2) Treatment of mobile boilers, mobile cranes
and gondolas
|
A. |
In the event that employers intend to install
mobile boilers, mobile cranes and gondolas
after extending the effective term
of an
inspection certificate, they must submit
an installation notification (an installation
report in case of mobile cranes) along
with
a document relating to the storage
of such
specified machines, etc., to the director
of the labour standards inspection
office
in charge.
|
B. |
In the event that a document relating to
the storage of the specified machines, etc.,
accompanies the installation notification,
the expiration date of the effective term
for the inspection certificate for the relevant
specified machines, etc., may be changed
to the following:
For mobile boilers and gondolas: The first
anniversary of the installation date, provided
that such date is within two years since
the MANUFACTURING INSPECTIONS (the second
anniversary of the MANUFACTURING INSPECTION
in case the end of the second year after
the MANUFACTURING INSPECTION is within one
year from the installation date);
For mobile cranes: The second anniversary
of the installation date, provided that such
date is within three years since the MANUFACTURING
INSPECTIONS (the third anniversary of the
MANUFACTURING INSPECTION in case the end
of the third year after the MANUFACTURING
INSPECTION is within two years from the installation
date).
In such cases, the submission date
of such
installation notification must be within
one month after the confirmed date
on which
such storage is completed.
|
C. |
In the event that the effective term of an
inspection certificate is changed,
the ledger
must record in the Remarks column that
the
machine is an approved machine.
Example: The effective term of a mobile
crane
inspection certificate for which the
Manufacturing-Time
inspection is passed on April 1, 2000:
(1) A document relating to the storage is
not attached:
Up to March 31, 2002
|
(2) A document relating to the storage is
attached: |
|
Installed on March 1, 2001: Up to February
28, 2003
Installed on May 1, 2001: Up
to March 31,
2003
Installed on May 1, 2002: Up
to March 31,
2003 |
|
Appendix:
APPROVAL Standards for the Storage of Specified
Machines, Etc.
APPROVAL standards for the storage of specified
machines, etc., are as follows:
1. Organization of Storage Management
|
(1) |
Departments or sections in charge of the
storage of specified machines, etc.,
must
be clearly defined.
|
(2) |
Personnel in charge of the storage of specified
machines, etc., must be clearly defined.
|
(3) |
The contents of a document indicating the
storage conditions of specified machines,
etc., and the procedures for issuing
same
must be clearly defined.
|
(4) |
A ledger recording the storage of specified
machines, etc., must be clearly maintained.
|
2. Place and Method for Storage
|
(1) Boilers and class I pressure vessels
|
A. |
These machines must be stored indoors in
principle, or covered with waterproof
sheets
when stored outdoors.
|
B |
The following measures to prevent rust and
corrosion must be taken on the inside
and
the outside of pressure-resistant portions:
(a) |
Rust-prevention painting |
(b) |
Anti-rusting agent or grease |
(c) |
Drying agent or rust-prevention vaporizer
|
(d) |
Sealed in nitrogen gas
|
|
C. |
Applying anti-rusting and rust-prevention
measures to the outside and to the
combustion
chamber.
|
(2) |
Mobile cranes and gondolas
|
A. |
Machines must to stored in places suitable
for specified storage conditions.
|
B. |
Oil painting and other measures must be applied
at regular intervals.
|
3. Inspections During Storage
|
(1) Frequency of inspections
|
|
Inspections must be made once for every three
months and at the time of shipment,
and maintenance
must be made as necessary.
|
(2) Inspection items
|
A. |
Boilers and class I pressure vessels
(a) |
Presence of rust or corrosion on pressure-resistant
portions |
(b) |
Volume of remaining drying agents |
|
B. |
Mobile cranes
(a) |
Presence of abnormalities in lubricating
oil or cooling water |
(b) |
Presence of damages to structural parts |
(c) |
Presence of leakage in piping |
(d) |
Confirming the operation of hoisting and
turning |
(e) |
Confirming the operation of safety devices |
(f) |
Presence of rusting on wire cables, etc. |
|
C. |
Gondolas
(a) |
Presence of damages to structural parts |
(b) |
Confirming the operation of lifting devices |
(c) |
Confirming the operation of safety devices |
(d) |
Presence of rusting on wire cables, etc. |
|
(3)Maintenance of inspection records
|
|
Inspection records during storage must be
maintained over three years from the date
of each inspection.
|
|